[SystemSafety] SIL ratings to be scrapped?

ECHARTE MELLADO JAVIER javier.echarte at altran.com
Thu Aug 22 09:20:13 CEST 2013


I have discussed this mater several times. I think that low demand criteria should disappear because it is usually a fallacious argument.

"However, an on-demand function usually requires a continuous-mode function to monitor the conditions whose status triggers the demand, and if this is built-in to the function itself, as it often is in E/E/PE systems, then the function becomes subject to continuous-mode SIL criteria. So there is much lower call for the demand-mode SIL criteria and it is plausible that they may disappear at some point."

-----Mensaje original-----
De: systemsafety-bounces at lists.techfak.uni-bielefeld.de [mailto:systemsafety-bounces at lists.techfak.uni-bielefeld.de] En nombre de Peter Bernard Ladkin
Enviado el: miércoles, 21 de agosto de 2013 16:47
Para: systemsafety at lists.techfak.uni-bielefeld.de
Asunto: Re: [SystemSafety] SIL ratings to be scrapped?

Chris,

On 8/21/13 4:25 PM, Chris Hills wrote:
> I have just been taking to one of my customers who do control systems 
> for industrial systems.  They have been told by someone they are doing a system for that SIL ratings will "soon be scrapped".
> Apparently "It will be replaced by ALARP".

When the system development is governed by IEC 61508 or its national equivalents (it is also an EN and these are taken by EU member countries as national standards), then there is no indication that SILs will disappear. The current edition of IEC 61508 is IEC 61508:2010 and the next maintenance action is due to start in 2014 and will likely take two years. Beyond that, it takes some time (up to a year) before a newly published standard becomes the only reference standard (there is a period of time in which both old and new editions are accepted). So, 2017 at the earliest.

I also see no movement, or even rumor, amongst my committee colleagues towards eliminating SILs from the next edition of IEC 61508.

Related, though, might be a concern about whether to eliminate the distinction between on-demand and continuous modes of operation. In contrast to some of my eminent colleagues, I think it is useful to distinguish between system functions which are on-demand and those which are continuous. However, an on-demand function usually requires a continuous-mode function to monitor the conditions whose status triggers the demand, and if this is built-in to the function itself, as it often is in E/E/PE systems, then the function becomes subject to continuous-mode SIL criteria. So there is much lower call for the demand-mode SIL criteria and it is plausible that they may disappear at some point.

PBL

--
Prof. Peter Bernard Ladkin, Faculty of Technology, University of Bielefeld, 33594 Bielefeld, Germany
Tel+msg +49 (0)521 880 7319  www.rvs.uni-bielefeld.de