[SystemSafety] SIL ratings to be scrapped?
RICQUE Bertrand (SAGEM DEFENSE SECURITE)
bertrand.ricque at sagem.com
Thu Aug 22 17:04:53 CEST 2013
Hi Gerry,
I grossly agree. This has been also extensively covered by Jean-Pierre Signoret's work.
My concern was more on the final objective of the standard and of the concept. You find industries for which, apparently, THR is the objective and then the PFD, in particular the PFDavg, is quickly a problem. You have industries for which the PFDavg is the unique objective whatever the resulting THR. These ones were the majority (not to stay almost the exclusivity) at the origin of 61508. It is thus not surprinsing to have a standard oriented on PFD (PFH a bit also) and not on THR. The industries needing THR have quickly acknowledged the issue by either modifying (.e.g railway) the standard (and IMHO this is a fundamental modification) or not adopting it at all (e.g. aerospace).
This is why one of my suggestions for edition 3 is to add a Route 3 based on THR for quantitative aspects and on consequences only for qualitative aspects (in particular software). This would open the standard to industrial sectors having today difficulties with it and at the same time better match the state of the art.
Bertrand RICQUE
Program Manager, Optronics and Defense Division
T +33 (0)1 58 11 96 82
M +33 (0)6 87 47 84 64
23 avenue Carnot
91300 MASSY - FRANCE
http://www.sagem-ds.com<http://www.sagem-ds.com/>
[cid:image001.jpg at 01CE9F59.B12B3E30]
From: Gerry R Creech [mailto:grcreech at ra.rockwell.com]
Sent: Thursday, August 22, 2013 4:53 PM
To: RICQUE Bertrand (SAGEM DEFENSE SECURITE)
Cc: System Safety List; systemsafety-bounces at lists.techfak.uni-bielefeld.de
Subject: Re: [SystemSafety] SIL ratings to be scrapped?
Bertrand,
I wasn't discussing it from a tolerable hazard rate point of view.
I was simply (although I agree, maybe too simply), pointing out that a high demand system is a "demand mode" system where the hazard rate based on a PFD crosses the hazard rate defined by PFH, therefore PFH gets used provided the system meets the high demand requirements.
The maximum demand rate is defined by the slowest diagnostic test interval that has been used in the analysis. On a low & high demand system the process safety time is often independent from the diagnostic test interval.
In a continuous system the minimum process safety time is defined by the maximum diagnostic time plus the time to achieve the safe state.
They both have their place, the demand system can make use and take credit for diagnostics that would be to slow for continuous mode applications. Continuous mode systems can be used for application where failure of the SIS will cause a hazard, which a demand system can't.
My personal belief is that it is important to chose the correct system to fit the application.
If we loose the distinction between the different types of operation I believe that we are likely to complicate the requirements to make sure all aspects have been covered.
(ok, lets not get into the discussion on what happens once in the shutdown state just at the moment :-).
Best regards,
Gerry Creech
From: "RICQUE Bertrand (SAGEM DEFENSE SECURITE)" <bertrand.ricque at sagem.com>
To: System Safety List <systemsafety at techfak.uni-bielefeld.de>
Date: 22/08/2013 15:26
Subject: Re: [SystemSafety] SIL ratings to be scrapped?
Sent by: systemsafety-bounces at lists.techfak.uni-bielefeld.de
________________________________
Well said Jens, and things have not that much evoluated. This is normal as there are still industries that fiercely reject any approach to MTTH as the consequences might be disturbing in terms of necessary engineering effort and of low results...
Bertrand RICQUE
Program Manager, Optronics and Defense Division
T +33 (0)1 58 11 96 82
M +33 (0)6 87 47 84 64
23 avenue Carnot
91300 MASSY - FRANCE
http://www.sagem-ds.com<http://www.sagem-ds.com/>
[cid:image001.jpg at 01CE9F59.B12B3E30]
From: systemsafety-bounces at lists.techfak.uni-bielefeld.de [mailto:systemsafety-bounces at lists.techfak.uni-bielefeld.de] On Behalf Of Braband, Jens
Sent: Thursday, August 22, 2013 3:55 PM
To: M Mencke; Gerry R Creech
Cc: System Safety List; systemsafety-bounces at lists.techfak.uni-bielefeld.de
Subject: Re: [SystemSafety] SIL ratings to be scrapped?
This discussion on operation modes has been extensively lead in the 90s and early 00s. I was chairing the CENELEC WG at that time that rewrote annex A of EN 50129. I think the problem is oversimplified here.
I would advise anyone really interested to go into the modeling details, e. g. as published by Prof. Sato in
Yoshimura, I., Sato, Y., Suyanma, K.: Safety Integrity Level Model for Safety-related Systems in Dynamic Demand State, Proceedings of the 2004 Asian Inter-national Workshop on Advanced Reliability Modeling (AIWARM 2004), Hiroshima, 577-584
We had a lot of discussions in this time, basically the same as in the 90s, and I also wrote a paper for Safecomp with colleagues from TÜV
Braband, J., vom Hövel, R. and Schäbe, H.: Probability of Failure on Demand - the Why and the How , in: Proc. SAFECOMP2009, Hamburg, 2009, 46-54
This sums up many discussions we had in the 90s when writing the EN 50129. These papers show that from a risk based perspective PFH and PFD are indeed two sides of the same coin and not so much different as suggested by IEC 61508. It explains also the reason why EN 50129 uses THR and NOT PFH. THR is an umbrella concept for both PFH and PFD and that is the main message.
Best regards
Jens Braband
PS I stated my personal technical opinion here, not necessarily that of my employer or any other organization.
Von: systemsafety-bounces at lists.techfak.uni-bielefeld.de [mailto:systemsafety-bounces at lists.techfak.uni-bielefeld.de] Im Auftrag von M Mencke
Gesendet: Donnerstag, 22. August 2013 15:22
An: Gerry R Creech
Cc: System Safety List; systemsafety-bounces at lists.techfak.uni-bielefeld.de
Betreff: Re: [SystemSafety] SIL ratings to be scrapped?
Yes. They are different. The objective of my previous email was to point out that the classification of operation modes for Safety functions into different categories (one category containing "High demand" and "Continuous" and the other "Low demand") in some standards and only referring to "Continuous" mode in others could lead to confusion. In IEC 61508-1, the PFH assigned for each SI level is the same for both "High demand" and "Continuous" mode, therefore grouping "High demand" and "Continuous" in the same category, at least as far as PFH is concerned.
As you just mentioned, "Continuous" mode and "High demand" mode are not the same. However, if you consider the text I extracted from the EN 50129 standard (it is a direct quote from the standard), the second point states:
"All demand mode systems can be modelled as continuous mode systems".
This gives the (perhaps incorrect) impression that "High demand" and "Continuous" could be considered to be equivalent, that is, according to what is suggested by the standard.
Why? Because a logical interpretation of the above sentence is that "Continuous" mode and "High demand" mode are in a single category, named by the standard as "Continuous". If you consider the definition of "High demand" mode and "Continuous" mode, for "High demand", the frequency of demands is greater than one per year, and for Continuous, the safety function retains the EUC in a safe state as part of normal operation. This indicates to me that a "High demand" mode is a frequency of demand anywhere between greater than one per year and less than normal operation, a "Continuous" frequency being the limit of this interval. The frequency of "Low demand" can never be placed in this frequency range, as it is less than or equal to one per year.
prEN 50126-2:2012<http://www.cenelec.eu/dyn/www/f?p=104:110:2614904360520594::::FSP_ORG_ID,FSP_LANG_ID,FSP_PROJECT:,25,21753> (page 39, section 10.2) makes reference to "continuous mode models". However, in drafts 1 - 5 of this standard I cannot find any definition of "continuous", "high demand", or other. It seems that these drafts are now in "In hands of WG 14". It may be a suggestion to include a definition of what "continuous mode" includes, or specify that the category "continuous" groups modes only in terms of the same PFH.
Regards.
2013/8/22 Gerry R Creech <grcreech at ra.rockwell.com<mailto:grcreech at ra.rockwell.com>>
Myriam,
Isn't 'high demand' also a demand mode, that happens to use PFH and different from continuous mode?
In continuous mode, we can only take credit for diagnostics that can detect a failure and carry out the specified action within the process safety time.
In high demand mode, we can take credit for diagnostics where the ratio of the test rate to the demand rate equals or exceeds 100.
Best regards,
Gerry Creech
From: M Mencke <menckem at gmail.com<mailto:menckem at gmail.com>>
To: Peter Bernard Ladkin <ladkin at rvs.uni-bielefeld.de<mailto:ladkin at rvs.uni-bielefeld.de>>
Cc: System Safety List <systemsafety at techfak.uni-bielefeld.de<mailto:systemsafety at techfak.uni-bielefeld.de>>
Date: 22/08/2013 11:10
Subject: Re: [SystemSafety] SIL ratings to be scrapped?
Sent by: systemsafety-bounces at lists.techfak.uni-bielefeld.de<mailto:systemsafety-bounces at lists.techfak.uni-bielefeld.de>
________________________________
Regarding the high demand and low demand mode, it makes sense to apply these modes for some elements. However, in the railway standards, the concept of low demand is already not being considered. In EN 50129, the following is stated:
"NOTE: In contrast to other standards the SIL table in this standard has only one column for
frequencies (formerly called high demand or continuous mode) and does not have a column for
failure probabilities on demand (formerly called demand mode). The reasons to restrict to one
mode are
· Less ambiguity in determination of SIL.
· All demand mode systems can be modelled as continuous mode systems.
· Continuous control and command signalling systems are clearly the majority in modern railway signalling applications.
The SIL table has been constructed taking into account other relevant international standards."
In my opinion, the existence of two different approaches to the application of the SIL concept, where one only considers high demand mode and the other considers both, contributes to the reasons why there are misunderstandings regarding the use of SIL. This is particularly true for engineers new to the industry or potential customers who consult the standard relevant to their sector in order to try to gain an understanding of the SIL concept.
Imagine a situation where a "newcomer" to the railway industry consults the railway standards for an overview of SILs, and their understanding of the SIL concept is gained based on the assumption that only one mode of operation is considered, the high demand mode. This engineer (or technician, manager, etc.) then decides that he would like to extend his knowledge and reads, for example, the IEC 61508 where the "high demand" and "low demand" modes are introduced. This does not appear to aid the reader in providing a clear explanation of the application of the concept. Your response may be "well, in that case the reader should read the available literature", to gain an in-depth understanding. However, this may not always be possible, due to time constraints, etc., particularly in the case of a customer or a manager.
Additionally, even though the standard argues that continuous demand are the majority in modern railway signalling applications, as Peter just mentioned, passenger emergency braking systems on trains are meant to be used only occasionally. Given that only high demand mode is considered in the railway standards, should the railway standard definition of "high demand" then be applied for this type of system, or is it required to refer "back" to IEC 61508?...
Note: I write in Hiberno English. For example, words ending in the suffix "ing" preceded by "l" are spelled with a double "l" rather than a single "l", as in "signalling", "modelling".
Regards,
Myriam.
2013/8/22 Peter Bernard Ladkin <ladkin at rvs.uni-bielefeld.de<mailto:ladkin at rvs.uni-bielefeld.de>>
To back up Martin's caveat with other reasons:
I would not argue for scrapping "low-demand" on the sole basis it is inappropriately applied - I think there need to be significantly more reasons than that.
Reactor SCRAM systems are only meant to be used occasionally. Similarly, passenger-emergency-braking systems on trains.
System functions which are invoked occasionally tend to not work when invoked. Emergency slides on commercial transport aircraft exits work as a rule-of-thumb about half the time, which is why the emergency-evacuation certification test is performed with only half the available exits.
So for such systems and functions there need to be defined proof tests and a defined interval for proof tests. And those intervals are dependent upon how often you think the demand for the function is likely to arise.
You don't have such things as proof tests or associated intervals for continuously-operating safety-relevant functions, such as fly-by-wire control systems or ETCS.
Now, I agree that such things as proof tests are not relevant for pure SW "elements" (to use the 61508 preferred terminology), but that SW mostly sits inside something which executes the function and for which proof tests are relevant. How are you going to deal with these differences appropriately if the standard scraps the distinction?
PBL
On 8/22/13 9:30 AM, Jensen, Martin Faurschou Jensen wrote:
I agree with the arguments below when it comes to systems, but we have to keep in mind that 61508 is also used for the development of single elements. For a sensor, designed and developed for use in a SIS, the demand mode makes sense, as this only needs to detect and report a situation, and does not need to contribute in maintaining the safe state afterwards.
-----Original Message-----
......On Behalf Of ECHARTE MELLADO JAVIER
Sent: 22. august 2013 09:20
To: Peter Bernard Ladkin; systemsafety at lists.techfak.uni-bielefeld.de<mailto:systemsafety at lists.techfak.uni-bielefeld.de>
Subject: Re: [SystemSafety] SIL ratings to be scrapped?
I have discussed this mater several times. I think that low demand criteria should disappear because it is usually a fallacious argument.
PBL
Prof. Peter Bernard Ladkin, Faculty of Technology, University of Bielefeld, 33594 Bielefeld, Germany
Tel+msg +49 (0)521 880 7319<tel:%2B49%20%280%29521%20880%207319> www.rvs.uni-bielefeld.de<http://www.rvs.uni-bielefeld.de/>
_______________________________________________
The System Safety Mailing List
systemsafety at TechFak.Uni-Bielefeld.DE<mailto:systemsafety at TechFak.Uni-Bielefeld.DE>
_______________________________________________
The System Safety Mailing List
systemsafety at TechFak.Uni-Bielefeld.DE<mailto:systemsafety at TechFak.Uni-Bielefeld.DE>
#
" Ce courriel et les documents qui lui sont joints peuvent contenir des informations confidentielles ou ayant un caractère privé. S'ils ne vous sont pas destinés, nous vous signalons qu'il est strictement interdit de les divulguer, de les reproduire ou d'en utiliser de quelque manière que ce soit le contenu. Si ce message vous a été transmis par erreur, merci d'en informer l'expéditeur et de supprimer immédiatement de votre système informatique ce courriel ainsi que tous les documents qui y sont attachés."
******
" This e-mail and any attached documents may contain confidential or proprietary information. If you are not the intended recipient, you are notified that any dissemination, copying of this e-mail and any attachments thereto or use of their contents by any means whatsoever is strictly prohibited. If you have received this e-mail in error, please advise the sender immediately and delete this e-mail and all attached documents from your computer system."
#_______________________________________________
The System Safety Mailing List
systemsafety at TechFak.Uni-Bielefeld.DE
#
" Ce courriel et les documents qui lui sont joints peuvent contenir des informations confidentielles ou ayant un caractère privé. S'ils ne vous sont pas destinés, nous vous signalons qu'il est strictement interdit de les divulguer, de les reproduire ou d'en utiliser de quelque manière que ce soit le contenu. Si ce message vous a été transmis par erreur, merci d'en informer l'expéditeur et de supprimer immédiatement de votre système informatique ce courriel ainsi que tous les documents qui y sont attachés."
******
" This e-mail and any attached documents may contain confidential or proprietary information. If you are not the intended recipient, you are notified that any dissemination, copying of this e-mail and any attachments thereto or use of their contents by any means whatsoever is strictly prohibited. If you have received this e-mail in error, please advise the sender immediately and delete this e-mail and all attached documents from your computer system."
#
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://lists.techfak.uni-bielefeld.de/mailman/private/systemsafety/attachments/20130822/9ec2dc41/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1835 bytes
Desc: image001.jpg
URL: <https://lists.techfak.uni-bielefeld.de/mailman/private/systemsafety/attachments/20130822/9ec2dc41/attachment-0001.jpg>
More information about the systemsafety
mailing list